2. Based on the diagram below, what are the 3 phase & Line to Ground fault currents seen at the recloser for faults at location A. G 20.78 kV | 12 KV Location A 3 Phase Fault = 1530A Line to Ground Fault = 840A
Added by Sarah C.
Close
Step 1
It shows a power system with a recloser and a fault location labeled as A. The voltage levels are given as 20.78 kV and 12 kV. Show more…
Show all steps
Your feedback will help us improve your experience
Surendra Kumar and 88 other Physics 102 Electricity and Magnetism educators are ready to help you.
Ask a new question
Labs
Want to see this concept in action?
Explore this concept interactively to see how it behaves as you change inputs.
Key Concepts
Recommended Videos
A 30 MVA, 11 kV generator has Z1, Z2 = j0.2 pu, and Z0 = j0.05 pu. A line-to-ground fault occurs on the generator terminals. (a) Find the fault current and line-to-line voltage during faulty conditions. Assume that the generator neutral is solidly grounded and that the generator is operating at no load and at rated voltage at the occurrence of the fault. (b) Find the line current for a 3-phase fault.
Madhur L.
A 50 MVA, 11 kV, three-phase alternator was subjected to different types of faults. The fault currents were: 1870 Amps for three-phase fault, 2590 Amps for L-L fault, and 4130 Amps for L-G fault. The alternator neutral is solidly grounded. Find the three sequence reactances of the alternator.
Supreeta N.
A symmetrical 3-phase short circuit occurs on the 22 kV bus bars of the circuit shown as a one-line diagram in the above figure. Calculate the fault current and the fault apparent power. 11 kV/132 kV 132 kV/22 kV Loads 25 MVA x' = 0.15 p.u. 30 MVA x = 0.09 p.u. 100 MVA x = 0.092 p.u. 5 MVA x = 0.02 p.u.
Recommended Textbooks
University Physics with Modern Physics
Physics: Principles with Applications
Fundamentals of Physics
Watch the video solution with this free unlock.
EMAIL
PASSWORD