The plot shown in Figure P3 below relates the operating frequency to the total power losses (due to hysteresis and eddy currents combined) per kilogram of core mass for a particular material used in laminated transformer construction. As indicated in Figure P3, the material is 0.356 [mm] thick electrical sheet steel. Compute the total core power loss, Pc, for a core constructed in an EI configuration with the material represented by the plot if:
a. The total core volume is Vc = 0.009 [m^3].
b. The stacking factor is SF = 0.90.
c. The M-36 sheet steel density is d = 7.70 [g/cm^3].
d. The transformer operates at a frequency of f = 100 [Hz].
e. The maximum flux density in the core is Bmax = 0.7 [T].