. A balanced three-phase, three wire 480 V supply has two loads.
The first load is delta connected and takes 30 kW at 80% lagging
power factor. The second load is delta connected and uses 24 kVA at
90% leading power factor. Find the readings of the two wattmeters
connected in lines A and C.
A. 30,000 & 21,600 W
B. 32, 680 & 18,920 W
C. 20,400 & 31,200
W
D. 28,940 & 22,660 W