A balanced three-phase, Y-connected 12.5 MVA, 30 kV (L-L) synchronous generator has a reactance of 12 per phase. Using the rated MVA and voltage as base values, determine the reactance in pu. OA. 0.66 0 B. 0.50 0 C. 0.60 0 D. 0.55
Added by Felipe G.
Close
Step 1
The base MVA is given as 12.5 MVA, and the base voltage is given as 30 kV (L-L). Show more…
Show all steps
Your feedback will help us improve your experience
Ivan Kochetkov and 91 other Physics 102 Electricity and Magnetism educators are ready to help you.
Ask a new question
Labs
Want to see this concept in action?
Explore this concept interactively to see how it behaves as you change inputs.
Key Concepts
Recommended Videos
A 50 MVA, 30 kV, three-phase, 60 Hz synchronous generator has a synchronous reactance of 0.9 Ω per phase and negligible resistance. The generator is delivering rated power at a 0.8 power factor lagging at the rated terminal voltage to an infinite bus. The power angle (δ) is Select one: a. 2.22° b. 9.13° c. 3.23° d. 1.58° e. 11.26°
Sri K.
Madhur L.
A three-phase, 12-kV, 60 Hz, 6-pole wye-connected synchronous generator has a synchronous reactance of 15 Ω per phase and negligible armature resistance. For a given field current, the open circuit voltage is 13 kV. Determine the following: A) Terminal Voltage B) Excitation voltage EA at maximum power C) The maximum power developed by the generator and pullout torque