Hi, for this problem, we are told to find the rating of a fan motor unit to want to buy and to also find the size of the fan and what the pressure difference across the fan will be.
00:16
Now, the electrical rating of a fine, i'll call it this, is simply equal to the effective fan power divided by the efficiency of the fan and motor connection.
00:39
Now, we were giving this efficiency as 50%.
00:44
So to find this electrical rating, all we need to do is to find the effective fan power.
00:54
Now, from the energy equation, i can simply write that the mass flow times this plus the kinetic energy correction factor times v1 square over 2 plus gz1 plus the effective fan power output is going to be equal to the same mass flow p2 over row plus alpha 2 v2 square over 2 plus gz2 now, if i model this fan this way, let this be my fan, and i put station one here and station two here.
01:58
You can see that at these very far locations, very far from the fan, i can simply write that p1 at this point is simply atmospheric pressure, also very far away from the fan.
02:11
P2 is also atmospheric pressure.
02:15
This is the inlet to the fan, this is the outlet.
02:20
Also, z1 here will be equal to z2.
02:24
The levels are the same both at the inlet and the outlet.
02:30
We see also that at this inlet position quite far away from the fan, we can see that v1 there is equal to zero.
02:40
Now, the problem also asked us to neglect the kinetic energy correction factors.
02:46
So i can just say that alpha 1 is 1 and alpha 2 is 1.
02:50
And if i apply all this, my equation becomes the effective work output of the fan is simply going to be equal to the mass flow rate times v2 squared over 2.
03:12
Now, what is the mass flow rate across the fan? it's simply the density of air times this.
03:22
But we know also that area times velocity is the same thing as what the flow rate, the voice, the volume.
03:28
Volume flow rates.
03:31
Now we are told that this fan changes the entire volume of air in the bathroom every 10 minutes.
03:40
What it means is that the mass flow rates would then be equal to the density of air times the volume of the bathroom changed every 10 minutes...