A single-phase 100-kVA, 2400/240-volt, 60-Hz distribution transformer is used as a step-down transformer. The load, which is connected to the 240-volt secondary winding, absorbs 80 kVA at 0.8 powerfactor lagging and is at 230 volts. Assuming an ideal transformer, calculate the following: (a) primaryvoltage, (b) load impedance, (c) load impedance referred to the primary, and (d) the real and reactivepower supplied to the primary winding