Problem 2: A 60 Hz, 75 kVA, 13.5 kV/240 V, single-phase ideal transformer is used to step-down the voltage of a distribution system. If the low-voltage side of the transformer is to be kept at a constant magnitude of |V2| = 240 V (rms), determine the following quantities: a) the value of the load impedance (connected to the low-voltage side) that will cause the transformer to be fully loaded; b) the value of the load impedance found in a) referred to the high-voltage side of the transformer; c) the value of the load current referred to the low-voltage side of the transformer; and d) the value of the load current referred to the high-voltage side of the transformer. Ans: a) |ZFL,s| = 0.768 Ω; b) |ZFL,p| = 2.430 kΩ; c) |ILoad,s| = 312.5 A (rms); d) |ILoad,p| = 5.556 A (rms).