00:01
Let's discuss this question here.
00:02
3 -phase overhead transmission line given to us.
00:06
So we need to determine the sending end line voltage and current by rigorous method.
00:14
Z is equal to 200 less than 80 degrees oms per phase.
00:25
Gamma is equal to 0 .013 less than 90 degrees oms per phase.
00:34
Fosphi is equal to 0 .8 lakh, vr is equal to 220 kilowatt, pr is equal to 80 megawatts, therefore, ir is equal to pr divided by under root 3, vr, fos 5.
01:00
This is equal to 80 multiplied by 10x to 6 divided by under root 3 multiplied by 3, 220 multiplied by 10 x to 3 multiplied by 0 .08.
01:14
So this is equal to 262 .43 amper.
01:26
So further, vr phase is equal to 220 multiplied by 10 raise to 3 divided by under root 3 and this is equal to 127 .02 kilowatt...