A $0.4 \mathrm{~m}$ diameter fan running at $970 \mathrm{rev} \mathrm{min}^{-1}$ is tested when the air temperature is $10^{\circ} \mathrm{C}$ and the barometric pressure is $772 \mathrm{~mm} \mathrm{Hg}$ and the following data are observed: $Q=0.7 \mathrm{~m}^{3} \mathrm{~s}^{-1}$; fan total pressure $=25 \mathrm{~mm}$ of water; shaft power $=250 \mathrm{~W}$
Find the corresponding volume flow, fan total pressure and shaft power of a geometrically similar fan of $1 \mathrm{~m}$ diameter, running at 500 rev $\min ^{-1}$ when the air temperature is $16^{\circ} \mathrm{C}$ and the barometric pressure is $760 \mathrm{~mm} \mathrm{Hg}$. Assume that the fan efficiency is unchanged.
$\left[5.64 \mathrm{~m}^{3} \mathrm{~s}^{-1}, 40 \mathrm{~mm}\right.$ of water, $\left.3.22 \mathrm{~kW}\right]$