Question
A plant consumes $60 \mathrm{kW}$ at a power factor of 0.75 lagging from a $240-\mathrm{V} \mathrm{rms} 60-\mathrm{Hz}$ line. Determine the value of the capacitor that when placed in parallel with the load will change the load power factor to 0.9 lagging.
Step 1
The power factor is given as 0.75 lagging, which means the angle is the arccosine of 0.75. This gives us an angle of 41.41 degrees. \[ \theta_{old} = \cos^{-1}(0.75) = 41.41^{\circ} \] Show more…
Show all steps
Your feedback will help us improve your experience
Narayan Hari and 97 other educators are ready to help you.
Ask a new question
Labs
Want to see this concept in action?
Explore this concept interactively to see how it behaves as you change inputs.
Key Concepts
Recommended Videos
The $60-\mathrm{Hz}$ line voltage for a $60-\mathrm{kW}, 0.76$ -pf lagging industrial load is $240\underline{/0^{\circ}}$ $\mathrm{V}$ rms. Find the value of capacitance that when placed in parallel with the load will raise the power factor to $0.9$ lagging.
A particular load has a pf of 0.8 lagging. The power delivered to the load is $40 \mathrm{kW}$ from a 220 -V rms 60 -Hz line. What value of capacitance placed in parallel with the load will raise the pf to 0.9 lagging?
A particular load has a pf of 0.8 lagging. The power delivered to the load is $40 \mathrm{kW}$ from a 270 -V $\mathrm{ms} 60$ -Hz line. What value of capacitance placed in parallel with the load will raise the pf to 0.9 lagging?