00:01
So the resistance in the line, r subline would be equaling 4 .50 times 10 to the negative 4th ums per meter multiplied by 6 .44 times 10 to the 5th meters.
00:23
This is giving us 290 ums.
00:27
We now know that here for part a, the average power transmitted would be equaling the rms voltage voltage.
00:46
Multiplied by the rms current.
00:51
Now we can then solve for the rms current.
00:55
This would be equaling the average power transmitted divided by the rms voltage and so we can say that the rms current is equaling 5 .00 times 10 to the 6th watts and this would be divided by 500 times 10 to the third volts and this is giving us 10 .0 amps.
01:29
And so we can then see that the average power loss would be equalling rms squared multiplied rms current squared multiplied by the resistance in the line.
01:44
And so this would be 10 .0 amps squared multiplied by 2090 ums and this is giving us 2 .90 times 10 to the 4th watts this would be our final answer for part a for part b then we can say the power input to the line would be power average input this would be equalling the rms current squared rather my apologies this would be equaling the average power transmitted plus the average power lost.
02:36
And so this would be equaling 5 .00 times 10 to the 6 watts plus 2 .90 times 10 to the 4th watts.
02:50
And so this is going to be equaling 5 .03 times 10 to the 6 watts.
03:00
And so now the fraction of input power lost during transmission would be, we can say, some fraction is going to be equaling the average power loss divided by the average power input.
03:20
So this would be 2 .90 times 10 to the fourth watts divided by 5 .03 times 10 to the 4 watts divided by 5 .03 times 10 to the 6 watts and this is giving us 0 .00577 or we can say 0 .577%.
03:47
So this would be our final answer for part b.
03:52
For part c, we know that it is impossible to deliver the needed power at the generator voltage of 4 .5, 4 .50 kilovolts...