0:00
Hello everyone.
00:01
Let us do the following question.
00:03
In the question we have given a wide delta three -phase transformer is connected to 60 kilowalt ampere load with the 0 .85 power factor and whose impedance is each face is connected with the impedance of 0 .05 plus j plus 0 .1 -hom.
00:20
Find the magnitude of line current at the load.
00:23
The line voltage at the secondary side of the transformer.
00:26
The line current at the primary side of the transformer.
00:30
Firstly, we will say that we will find this value at the load.
00:35
We will follow this equation at the load.
00:37
At the load, this can be written as bl.
00:40
Value of this can be written as 240 volt.
00:43
Voltage of this is written as a, b.
00:46
If we have to write voltage of a with respect to n, this value can be written as bl under the root 3.
00:54
If we will find this value, we will get this value as 138 .56.
01:00
Value of this is 138 .56 volts.
01:02
Next, if we find complex power, then value of this is under the root 3 vl into il and then we will get the value of for il as 60 ,000 as given in the question divided by 240 under the root 3.
01:21
Value of this can be written as 144 .34 ampere.
01:26
This is the value.
01:28
Now in the second question, in the second question, in the second part we have to find v primary voltage along scatry circuit.
01:36
So we will say that let value of bn is can be written as v an into zero degree.
01:44
This can be written.
01:45
If we write this value, this can be written as 138 .56 into zero degree.
01:51
If we have to find value of course theta, this is equals to power factor or power factor is given in the question 0 .85.
02:00
From this, we will write value of theta as 31 .79 degree...