Question number one double three.
00:03
Air is heated and dehumidified in an air conditioning system consisting of a heating section and an evaporative cooler.
00:12
The temperature and the relative humidity of the air when it leaves the heating section, the rate of heat transfer in the heating section and the rate of water added to the air in the evaporative cooler are to be determined.
00:26
So firstly, i will draw a drawing.
00:34
This is the heating section and this is the humidifier where water sprinkles.
00:57
Here enters this portion.
01:01
Entering parameters are 15 degree temperature, 55 % relative humidity and 30 cubic meter per minute flow rate and the outside temperature is to know.
01:23
25 degree and 45 % relative humidity.
01:30
Now, assume the three conditions.
01:33
This is a steady flow process and thus the mass flow rate of dry air remains constant during the entire process.
01:39
So m .a1 is equal to m .a2 is equal to m .a.
01:49
Second, dry air and water vapors are ideal gases.
01:53
Third one kinetic and potential energy changes are negligible so as i'm assuming the wet bulb temperature of air remains constant during the evaporative cooling process the properties of air at various states are determined from the psychometric charts according to which t1 is equal to 15 degrees centigrade and relative humidity at the entry point is equal to 55 % according to psychometric charts and these available values h1 is equal to 29 .8 mega 1 or specific humidity is equal to 0 .00581 whereas v1 or the mass floor rate rate per kg volume per k .0 .824 mass floor rate per minute meter cube per kilogram as w2 is equal to w1 temperature of wet valve 2 is equal to temperature of wet wb3 so here we get the values g2 is equal to 32 .5 centigrade while the relative humidity and the airway is 19 .2 percent here h2 equal to h3 is equal to h3 is equal to to 47 .8 kilo joule per kilogram of dry air.
04:09
After that, t3 is equal to 25 degrees...