00:01
Okay, so we're generating power at 24 kilovolts at a plant that's located 85 kilometers from a town.
00:08
The town requires 65 megawatts of power at 12 kilovolts.
00:13
We have two transmission lines from the plant to the town, and each of these has a resistance of 0 .1 oms per kilometer.
00:20
So we're given the resistance per unit length.
00:23
We want to know what the output voltage of the transformer at the generating plant needs to be for an overall transmission efficiency of 98 .5%.
00:32
This is, of course, assuming a perfect transformer.
00:37
So the power generated by the plant, the power generated by the plant, is going to be the total power that the town needs, so the power the town needs, which is 65 megawatts here, over the efficiency.
00:56
So the plant will need to generate more power than the town needs because some power is lost to the lines.
01:03
And if we calculate what this fraction is, so it'll be 65 over 0 .985, this works out to be 65 .98 megawatts of energy.
01:17
So that's how much power the plant needs to generate...