3. A 400 V, 3-ph 4 wire star connected system supplies 3 resistive loads of 15 KW, 20 KW and 25 KW in the Red, Yellow and Blue phases respectively. Determine the current flowing in each of the four conductors.
Added by Jason M.
Close
Step 1
The line-to-line voltage is given as 400V. For a star connection, the line-to-neutral voltage \( V_L \) is given by: \[ V_L = \frac{V_{LL}}{\sqrt{3}} = \frac{400}{\sqrt{3}} \approx 230.94 \, \text{V} \] Show more…