A heat pump is installed to keep a building warm by absorbing heat from a nearby geothermal source during steady-state operation. Hot water (Geo.water) at 61°C enters the evaporator section of the heat pump and leaves at 41°C. Refrigerant 22 is used as the working fluid in the heat pump and enters the evaporator at a rate of 0.062 kg/s. The refrigerant leaves the evaporator at the same pressure as a saturated vapor. The power consumed by the compressor of the heat pump is measured at 2.7 kW. Figure Q2b shows the schematics of the system.
Condenser
Expansion valve
Compressor
Evaporator
41°C
Sat. vapor
Geo.water
Figure Q2b: Schematics of the heat pump
Determine:
1. The mass flow rate of the water from the geothermal source [5 Marks]
2. The rate of heat supply to the commercial facility space through the condenser [5 Marks]
3. The coefficient of performance (COP) of the heat pump [5 Marks]
4. The minimum theoretical power input to the compressor for the same rate of heat supply to the conditioned space [5 Marks]