00:01
To check the relay operation condition for the bias differential protection system and the determine the required mvf fault, we are following here three steps.
00:11
So the first, we are checking the relay operation condition, relay operation condition.
00:21
So calculating the restarting current and bias differential current.
00:25
The restating current is the sum of the current transformer, secondary's current and the 132 kv side when the fault is outside the predicted zone.
00:37
So we are first seeing that i, restating, so it is 250 divided by 5, it is in ampere, plus 250 divided by 5 because we have 3 and plus this is 250 divided by 5.
01:00
So we will get here, we calculated this is 150 ampere.
01:05
So since there is three phase fault.
01:09
Now we are seeing the bias current.
01:11
So the bias differential current is the restraining current multiplied by the bias percentage.
01:17
So this is i bias is b multiplied by the i restraining current.
01:26
So this is the value of b that is bias percentage given to us 0 .20 and we will multiply it by the i restraining.
01:35
So this is when we calculate this, this will be 30 ampere.
01:39
Now we will calculate the differential current.
01:42
So i differential, so the differential current is the sum of the ct secondary's current and the 33 kv side when the fault occurs.
01:55
So this will be 600 divided by 5, this is an ampere plus 600 divided by 5 plus 600 divided by 5 because here is three phase fault and when we will calculate this, we will get 360 ampere, the differential current.
02:21
Now we will check the relay operation condition.
02:24
So for the relay to operate and re -transferred, the following condition must be made.
02:30
So it is i differential minus i biased.
02:37
So magnitude of it should be greater than the i bias, difference in magnitude of this will be i bias, should be greater than i bias.
02:50
So let's see it.
02:50
So differential current 360 minus bias current it is 30 and if we see it should be greater than 30 ampere.
03:00
So when we will calculate this, this is 330 ampere and it is greater than 30 ampere...