Question
Two industrial plants represent balanced three-phase loads. The plants receive their power from a balanced three-phase source with a line voltage of $4.6 \mathrm{kV}$ rms. Plant 1 is rated at $300 \mathrm{kVA}, 0.8 \mathrm{PF}$ lagging, and plant 2 is rated at $350 \mathrm{kVA}, 0.84 \mathrm{PF}$ lagging. Determine the power line current.
Step 1
For Plant 1: \[ S_1 = 300 \, \text{kVA} \] For Plant 2: \[ S_2 = 350 \, \text{kVA} \] Total apparent power: \[ S_{total} = S_1 + S_2 = 300 \, \text{kVA} + 350 \, \text{kVA} = 650 \, \text{kVA} \] Show more…
Show all steps
Your feedback will help us improve your experience
Narayan Hari and 96 other educators are ready to help you.
Ask a new question
Labs
Want to see this concept in action?
Explore this concept interactively to see how it behaves as you change inputs.
Key Concepts
Recommended Videos
Two small industrial plants represent balanced three-phase loads. The plants receive their power from a balanced three-phase source with a line voltage of $4.6 \mathrm{kV}$ rms. Plant 1 is rated at $300 \mathrm{kVA}, 0.8$ pf lagging, and plant 2 is rated at $350 \mathrm{kVA}, 0.8 \mathrm{pf}$ lagging. Determine the power line current.
A balanced three-phase source serves two loads: Load $1: 36 \mathrm{kVA}$ at 0.8 pf lagging Load $2: 18 \mathrm{kVA}$ at 0.6 pf lagging The line voltage at the load is $208 \mathrm{V}$ rms at $60 \mathrm{Hz}$. Find the line current and the combined power factor at the load.
A small shopping center contains three stores that represent three balanced three-phase loads. The power lines to the shopping center represent a three-phase source with a line voltage of $13.8 \mathrm{kV} \mathrm{rms}$. The three loads are Load $1: 400 \mathrm{kVA}$ at $0.9 \mathrm{pf}$ lagging Load $2: 200 \mathrm{kVA}$ at $0.85 \mathrm{pf}$ lagging Load $3: 100 \mathrm{kVA}$ at 0.90 pf lagging Find the power line current.
Transcript
Watch the video solution with this free unlock.
EMAIL
PASSWORD