Question
Two small industries located side-by-side are fed from a three-phase balanced $60 \mathrm{~Hz}$ source with a line voltage of $208 \mathrm{~V}$ rms. Load #1 consumes $24 \mathrm{~kW}$ at $0.75 \mathrm{PF}$ lagging and load #2 consumes $16 \mathrm{~kW}$ at $0.88 \mathrm{PF}$ lagging. Determine the current in the line that serves both loads.
Step 1
Load #1 consumes \( P_1 = 24 \, \text{kW} \) and Load #2 consumes \( P_2 = 16 \, \text{kW} \). Total real power \( P_{total} = P_1 + P_2 = 24 \, \text{kW} + 16 \, \text{kW} = 40 \, \text{kW} \). Show more…
Show all steps