Question
The power consumed by an industrial load is $120 \mathrm{~kW}$ at $0.70 \mathrm{PF}$ lagging from a $480 \mathrm{~V}$ rms line. If the transmission line resistance between the generator and the load is $0.14 \Omega$, find the power that must be supplied by the power company.
Step 1
The apparent power can be calculated using the formula: \[ S = \frac{P}{PF} \] where \( P = 120 \, \text{kW} \) and \( PF = 0.70 \). \[ S = \frac{120 \, \text{kW}}{0.70} = 171.43 \, \text{kVA} \] Show more…
Show all steps
Your feedback will help us improve your experience
Narayan Hari and 85 other educators are ready to help you.
Ask a new question
Labs
Want to see this concept in action?
Explore this concept interactively to see how it behaves as you change inputs.
Key Concepts
Recommended Videos
The power company supplies $80 \mathrm{kW}$ to an industrial load. The load draws 220 A rms from the transmission line. If the load voltage is $440 \mathrm{V} \mathrm{rms}$ and the load power factor is 0.8 lagging, find the losses in the transmission line.
The power company must generate $100 \mathrm{kW}$ to supply an industrial load with $94 \mathrm{kW}$ through a transmission line with $0.09-\Omega$ resistance. If the load power factor is 0.83 lagging, find the load voltage.
An industrial load consumes 88 kW at a power factor of 0.707 lagging from a 480-V rms line. The transmission line resistance is 0.08 Ω. Determine the complex power supplied by the power company. Answer: S = 93.4 kW + j88 kVAR.